[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: How much light on a circuit?
> Here is another question. My house was wired in 68. My fish-room and
> a couple of other rooms are all on the same 15 amp circuit. Is there a
> way to know how much light I can plug in back there before I have to
> call either an electrician or the fire department? (Either one would have
Watts are calculated by multiplying voltage times current. Your 15 amp
circuit can therefore handle a maximum of about 115 x 15 = 1725 watts.
Naturally, you would not want to run the circuit at the very maximum wattage
available. For safety's sake, it would be wise to derate the outlet to
approximately 1500 watts maximum. Now you must go around and calculate all
the wattage of everything plugged into that circuit, including the loads in
the other rooms that are on the same line. Add them all up, and that's how
much load is being drawn. Whatever is left over is what's available for your
aquarium. Be sure to take into account that fluorescent ballasts are
inefficient, so that a 40 watt tube, say, will actually pull about 80 watts
due to losses in the ballast. (That's not precisely correct, but includes a
safety factor.) After adding everything up, you'll know whether you're
within limits or not. If not, perhaps you can move some of the loads in the
other rooms to different circuits? By the way, 15 amp circuits no longer
meet the National Electric Code, with 20 amp circuits being "standard." I'm
trying to remember back, but I seem to recall that was the rule back in 1968
as well. If you can look at the actual wire running to the circuit, see if
you can read the size of the wire. There will be something stamped on the
wire that will look like "14/3" or "12/3" or similar. If the wire is 14
gauge (the 14 in 14/3), then that circuit is indeed limited to 15 amps. If
the wire is 12 gauge, it can actually handle 20 amps, and you could safely
change the fuse or circuit breaker from 15 amps to 20 amps. You may also
have to upgrade the socket itself if it's only a 15 amp socket. If there's
any doubt in your mind about how to interpret any of this, hire a licensed
electrician. He can run a larger line for you.