>>Electrical work:  W = VA = 12*8.5 = 102 watts.
>>W/Q >= 1 - Tc/Th, so Q <= W/(1 - Tc/Th).
>>Tc = (0 + 273) K = 273 K.  Th = (50 + 273) K = 323 K.
>>Therefore, Q <= 102 watts/(1 - 273/323) = 659 watts.
>>
>>So this particular device could transfer _at most_ 659 watts (2249
Btu/hr).
>>The actual amount is probably a lot less.
>>
>>If we knew the actual heat transfer rate, we could compare the efficiency
of
>>the Peltier junction with that of an ordinary refrigerator or air
>>conditioner.  (Just convert the heat transfer from Btu/hr to watts.)
>
>
>OK, now calculate that for a gallon of water (assuming no heat is lost
>through glass or elswhere).  How many degrees temp can a gallon of water be
>lowered with that much power?  I have no clue how to calculate this.


If there's no heat leakage (yeah, right), then any amount of cooling, no
matter how small, could reach the temperature that you want.  The difference
is how long it would take.  Let's say that the Peltier junction has a heat
transfer capacity of only 50 watts (171 Btu/hr).  A Btu is defined as the
amount of heat needed to raise 1 pound of water by one degree Fahrenheit,
and there are about 8.5 lbs of water in a gallon.  If you have a 20 gallon
tank at 80 deg F and want to lower it to 60 deg F, the amount of heat you
need to remove is the following:

(20 gal H2O)(8.5 lb H2O/gal)(1 Btu/lb H2O/deg F)(80 deg F - 60 deg F) =
3400 Btu.

The amount of time needed to go from 60 to 80 deg F would be:
3400 Btu/(171 Btu/hr) = 19.9 hr.

Ouch!  And that's assuming that no heat leaks into the aquarium, which we
know isn't the case.  This doesn't tell us how much power we would need to
_keep_ the tank at the lower temperature, but it gives a good indication
that 50 watts of cooling won't be enough.

If you want to know how much power is needed to maintain a low temperature,
it is necessary to take into account the heat leakage into the tank from the
outside air.  To do this, we can take advantage of the fact that the rate of
heat transfer is directly proportional to the surface area, and also
directly proportional to the difference between the temperatures of the
aquarium and its surroundings.

Mathematically:  Q = U*A*(To - Ti).

Q is the rate of heat transfer, A is the surface area of the tank, To is the
temperature of the outside air, and Ti is the temperature inside the
aquarium.  U is an experimentally determined number called the overall heat
transfer coefficient, and it is usually a constant.  (If I remember
correctly, the R-value of home insulation is the reciprocal of this number,
or 1/U.)

For our purposes, it is not necessary to separate the specific heat transfer
and area terms, so we will combine them into a single parameter UA, which
has units of watts/deg C or Btu/hr/deg F.

If you know UA for your aquarium, then the rate of heat transfer required is
easy to determine.  I have to work out a few equations first, but I'll post
another message explaining how you can do a simple experiment to determine
the UA of your aquarium.

------------------------------------------------------------
[\   Andrew Dalton
[\[\
[\  [\
[\[\[\[\
[\      [\
[\[\    [\[\
[\  [\  [\  [\
[\[\[\[\[\[\[\[\
[\              [\
[\[\            [\[\
[\  [\          [\  [\
[\[\[\[\        [\[\[\[\
[\      [\      [\      [\
[\[\    [\[\    [\[\    [\[\
[\  [\  [\  [\  [\  [\  [\  [\
[\[\[\[\[\[\[\[\[\[\[\[\[\[\[\[\
------------------------------------------------------------